VHDL provides two major object types to hold data, namel signal and variable, but I can't find anywhere that is clear on when to use one data-type over the other. Can anyone shed some light on their strengths/limitations/scope/synthesis/situations in which using one would be better than the other?

Signals can be used to communicate values between processes. Variables cannot. There are shared variables which can in older compilers, but you really are asking for problems (with race conditions) if you do that - unless you use protected types which are a bit like classes. Then they are same to use for communication, but not (as far as I know) synthesisable.
This fundamental restriction on communication comes from the way updates on signals and variables work.
The big distinction comes because variables update immediately they are assigned to (with the := operator). Signals have an update scheduled when assigned to (with the <= operator) but the value that anyone sees when they read the signal will not change until some time passes.
(Aside: That amount of time could be as small as a delta cycle, which is the smallest amount of time in a VHDL simuator - no "real" time passes. Something like wait for 0 ps; causes the simulator to wait for the next delta cycle before continuing.)
If you need the same logic to feed into multiple flipflops a variable is a good way of factoring that logic into a single point, rather than copying/pasting code.
In terms of logic, within a clocked process, signals always infer a flipflop. Variables can be used for both combinatorial logic and inferring a flipflop. Sometimes both for the same variable. Some think this confusing, personally, I think it's fine:
process (clk)
variable something : std_logic;
if rising_edge(clk) then
if reset = '1' then
something := '0';
else
output_b <= something or input c; -- using the previous clock's value of 'something' infers a register
something := input_a and input_b; -- comb. logic for a new value
output_a <= something or input_c; -- which is used immediately, not registered here
end if;
end if;
end process;
One thing to watch using variables is that because if they are read after they are written, no register output is used, you can get long chains of logic which can lead to missing your fmax target
One thing to watch using signals (in clocked processes) is that they always infer a register, and hence leads to latency.

As others have said signals get updated with their new value at the end of the time slice, but variables are updated immediately.
// inside some process
// varA = sigA = 0. sigB = 2
varA := sigB + 1; // varA is now 3
sigC <= varA + 1; // sigC will be 4
sigA <= sigB + 1; // sigA will be 3
sigD <= sigA + 1; // sigD will be 1 (original sigA + 1)
For hardware design, I use variables very infrequently. It's normally when I'm hacking in some feature that really needs the code to be re-factored, but I'm on a deadline. I avoid them because I find the mental model of working with signals and variables too different to live nicely in one piece of code. That's not to say it can't be done, but I think most RTL engineers avoid mixing... and you can't avoid signals.
Other points:
Signals have entity scoping. Variables are local to the process.
Both synthesize

Related

PLC Object Oriented Programming - Using methods

I'm writing a program for a Schneider PLC using structured text, and I'm trying to do it using object oriented programming.
Being a newbie in PLC programming, I wrote a simple test program such a this:
okFlag:=myObject.aMethod();
IF okFlag THEN
// it's ok, go on
ELSE
// error handling
END_IF
aMethod must perform some operations, wait for the result (there is a "time-out" check to avoid deadlocks) and return TRUE or FALSE
This is what I expected during program execution
1) when the okFlag:=myObject.aMethod(); is reached, the code inside aMethod is executed until a result is returned. When I say "executed" I mean that in the next scan cycle the execution of aMethodcontinues from the point it had reached before.
2) the result of method calling is checked and the main flow of the program is executed
and this is what happens:
1) aMethod is executed but the program flow continues. That is, when it reaches the end of aMethod a value it's returned, even if the events that aMethod should wait for are still executing.
2) on the next cycle, aMethod is called again and restarts from the beginning
This is the first solution I found:
VAR_STATIC
imBusy: BOOL
END_VAR
METHOD aMethod: INT;
IF NOT(imBusy) THEN
imBusy:=FALSE;
aMethod:=-1; // result of method while in progress
ELSE
aMethod:=-1;
<rest of code. If everything is ok, the result is 0, otherwise is 1>
END_IF
imBusy:=aMethod<0;
and the main program:
CASE (myObject.aMethod()) OF
0: // it's ok, go on
1: // error handling
ELSE
// still executing...
END_CASE
and this seems to work, but I don't know if it's the right approach.
There are some libraries from Schneider which use methods that return boolean and seem to work as I expected in my program. That is: when the cycle reaches the call to method for the first time the program flow is "deviated" somehow so that in the next cycle it enters again the method until it's finished. It's there a way to have this behaviour ?
generally OOP isn't the approach that people would take when using IEC61131 languages. Your best bet is probably to implement your code as a state machine. I've used this approach in the past as a way of simplifying a complex sequence so that it is easier for plant maintainers to interpret.
Typically what I would recommend if you are going to take this approach is to try to segregate your state machine itself from your working code; you can implement a state machine of X steps, and then have your working code reference the statemachine step.
A simple example might look like:
stepNo := 0;
IF (start AND stepNo = 0) THEN
StepNo = 1;
END_IF;
(* there's a shortcut unity operation for resetting this array to zeroes which is faster, but I can't remember it off the top of my head... *)
ActiveStepArray := BlankStepArray;
IF stepNo > 0 THEN
IF StepComplete[stepNo] THEN
stepNo := stepNo +1;
END_IF;
ActiveStepArray[stepNo] := true;
END_IF;
Then in other code sections you can put...
IF ActiveStep[1] THEN
(* Do something *)
StepComplete[1] := true;
END_IF;
IF ActiveStep[2] THEN
(* Do Something *)
StepComplete[2] := true;
END_IF;
(* etc *)
The nice thing about this approach is that you can actually put all of the state machine code (including jumps, resets etc) into a DFB, test it and then shelve it, and then just use the active step, step complete, and any other inputs you require.
Your code is still always going to execute an entire section of logic, but if you really want to avoid that then you'll have to use a lot of IF statements, which will impede readability.
Hope that helps.
Why not use SFC it makes your live easier in many cases, since it is state machine language itself. Do subprogram, wait condition do another .. rince and repeat. :)
Don't hang just for ST, the other IEC languages are better in some other tasks and keep thing as clear as possible. There should be not so much "this is my cake" mentality on the industrial PLC programming circles as it is on the many other programming fields, since application timeline can be 40 years and you left the firm 20 years ago to better job and programs are almost always location/customer or atleast hardware specific.
http://www.automation.com/pdf_articles/IEC_Programming_Thayer_L.pdf

clock pulse generator for a PLC

I am working with PLCs trying to design a water tank. On one section of the design I am asked to create a clock pulse generator. I am currently trying to do this using ladder diagrams.
I believe I have the logic correct just cant seem to put it together. I want a counter to count the clock pulses that I generate, then I store these pulese in a data memory to ensure the count is retained if the system is switched off and on.
question is how do I design this clock pulse generator.
Kind regards
There are a few different ways to create a pulse generator (or commonly known in the plc world as a BLINK timer). As a matter of fact many plc programming softwares have this function block built in to their function block libraries. But if they don't or you just want to make your own you can do something like this
VAR
ton1: TON;
ton2: TON;
StartPulse: BOOL;
startPulseTrig: R_TRIG;
LatchPulseInitial: BOOL;
PulseOutput: BOOL;
Timer1Done: BOOL;
Timer2Done: BOOL;
PulseWidth:TIME:=t#500ms;
END_VAR
If you would like to count the number of pulses and store this value to a variable you can use a simple CTU (counter up) block available in all plc languages.
Review of functionality
The StartPulse variable can be anything you want that will start the counter. In my case I just used an internal bool variable that I turned on. If you want this timer to start automatically when the plc starts then just initialize this variable to true. Because StartPulse only works on the rising edge of the signal the LatchPulseInitial coil will only ever be set once.
When the LatchPulseInitial variable goes true this will start ton1 a Timer On Delay (TON) function block. This will delay the output of the block from turning on for the time of PT (in my case I have 500ms).
After 500ms has expired the ton1 outputs will turn on. this will turn on the Timer1Done variable and turn off the Timer2Done and LatchPulseInitial. Now that LatchPulseInitial has been turned off it will never interfere with the program again since it can only be turned on by the rising edge of StartPulse. Note: once the block has reached PT the outputs will stay on until the input to the block is removed.
Since Timer1Done is now on ton2 will start counting until PT is reached. Once PT is reached the outputs for that block will turn on. This will reset Timer1Done and set Timer2Done This will start ton1 again and thus starting the whole process over.
For the PulseOutput, which is the actual pulse output you are looking for, I have this being set to true when Timer2Done is true. This is because when this variable is true it is the high state of the pulse generator. When Timer1Done is true it is the low state of the pulse generator.
When the PulseOutput goes true it will trigger the input on the CTU which will increment the count of the variable in CV (current value) by 1.
If you are going to be using this logic in numerous places in your program or you plan on reusing it in the future I would make this into its own function block so you won't have to repeat this logic everytime you want to make this type of timer.
Once I had to create a BLINK FB. It is written in Structured Text. But it is suitable to use in a ladder logic program and IN/OUT Variables are named like TON style. The Blink starts with Q = TRUE. If you want to start with FALSE just invert Q and switch the Times!
FUNCTION_BLOCK BLINK
VAR_INPUT
IN : BOOL;
PT_ON : TIME;
PT_OFF : TIME;
END_VAR
VAR_OUTPUT
Q : BOOL;
ET : TIME;
END_VAR
VAR
rtIN : R_TRIG;
tonBlink : TON;
END_VAR
rtIN(CLK := IN);
IF tonBlink.Q OR rtIN.Q THEN
(*Toggle Output*)
Q := NOT Q;
(*Timer Reset call, important to call timer twice in same cycle for correct Blink Time*)
tonBlink(IN:= FALSE);
(*Set corresponding Time*)
IF Q THEN
tonBlink.PT := PT_ON;
ELSE
tonBlink.PT := PT_OFF;
END_IF
END_IF
(*Timer Run call*)
tonBlink(IN:= IN);
IF IN THEN
ET := tonBlink.ET;
ELSE
ET := T#0S;
Q := FALSE;
END_IF
In my opinion, this is the most straightforward way to do it, using 1 timer, up counter and modulo operator:
Blink function in ladder
Also note, if your PLC doesnt have modulo, then multiply by -1 each time.

vhdl how to use an entity within a process

I'm having difficulties to understand how I could utilize a sequential logic entity in the process of another. This process is a state-machine which on each clock signal either reads values from the input, or performs calculations. These calculation take many iterations to complete. However, each iteration is supposed to utilize a sub-entity, which is defined using the same principles as the above one (two-state state-machine, clock-based iterations), to obtain some results needed in the same iteration.
As I see it, I have two options:
implementing the subentity in a separate process within the main entity and finding a way to halt the main process and sync it with the subentity execution - this would mean using the clock signal of the main entity
implementing the subentity within the process of the main entity (basically something like a function call) and finding a way to halt the main process until subentity execution completes - this seems to me hardly doable using the main clock signal
None of them seems very appealing and rather complex, so I'm asking for some experienced insight and clarification. I really hope that there is a more conventional way that I'm missing.
"Entity" is an unfortunate choice of word here, as it suggests a VHDL Entity which may or may not be what you want.
You are thinking along roughly the right lines however, but it is a little unclear what you mean by "appealing"; so your goals are unclear and that makes it difficult to help.
To take your two approaches separately :
(1) Separate processes are a valid approach to dividing up tasks. They will naturally operate in parallel. In a synchronous design (best practice, safest and simplest - not universal but you need a compelling reason to do anything else) they will normally both be clocked by the same system clock.
When you need to synchronise them, you can, using extra "handshaking" signals. Typically your main SM would start the subsystem, wait until the subsystem acknowledged, wait again until the subsystem was done, and use the result.
main_sm : process(clk)
begin
if rising_edge(clk) then
case state is
...
when start_op =>
subsystem_start <= '1';
if subsystem_busy = '1' then
state <= wait_subsystem;
end if;
when wait_subsystem <=
subsystem_start <= '0';
if subsystem_busy = '0' then
state <= use_result;
end if;
when use_result => -- carry on processing
...
end case;
end if;
end process main_sm;
It should be clear how to write the subsystem to match...
This is most useful where the subsystem processing takes a large, variable or unknown time to complete - perhaps sending characters to a UART, or a serial divider. With care, it can also allow several top level processes to access the subsystem to save hardware (obviously the subsystem handshaking logic only responds to one process at a time!)
(2) If the sub-entity is to be implemented in the process, it should be written as a subprogram, i.e. as you speculate, a procedure or function. If it is declared local to the process it has access to that process's environment; otherwise you can pass it parameters. This is simplest when the subprogram can complete within the current clock cycle; often you can structure the code so that it can.
Try the following in your synthesis tool:
main_sm : process(clk)
procedure wait_here (level : std_logic; nextstate : state_type) is
begin
subsystem_start <= level;
if subsystem_busy = level then
state <= nextstate;
end if;
end wait_here;
begin
...
when start_op =>
wait_here('1', wait_subsystem);
when wait_subsystem <=
wait_here('0', use_result);
This rewrite of the handshaking above ought to work and in some synth tools it will, but others may not provide good synthesis support for subprograms.
You can use subprograms spanning multiple clock cycles in processes in simulation; the trick is to eliminate the sensitivity list and use
wait until rising_edge(clk);
instead. This is also potentially synthesisable, and can be used e.g. in a loop in a procedure. However some synthesis tools reject it, and Xilinx XST for one is actually getting worse, rather than better, in support for it.

'if' vs 'when' for making multiplexer

i have been told to use 'when' statement to make multiplexer but not use 'if' statement as it will cause timing errors...
i don't understand this ...
so what is the difference between 'if' and 'when' ? and do they map to the same thing in hardware ?
OK, lets discuss some points at first on the difference between if and when statements:
Both are called Dataflow Design Elements.
when statement
concurrent statement
not used in process, used only in architecture as process is sequential execution
if statement
sequential statement
used in process as it is sequential statement, and not used outside the process
And you know multiplexer is a component don't need process block, as its behavior doesn't change with changing its input, so it will be outside process, so you have to write it using when statement as it is concurrent statement.. And if you wrote it with if statement, timing errors may occur. Also all the references and also Xilinx help (if you are using Xilinx) are writing the Multiplexer block using when statement not if statement
Reference: Digital Design Priciples & Practices, John F. Wakerly, 3rd Edition
See these:
VHDL concurrent statements, which includes when.
VHDL sequential statements, which includes if.
Basically, if is sequential, and when is concurrent. They do not map to the same thing in hardware... This page describes, at the bottom, some of the special considerations needed to synthesize an if statement.
Both coding styles are totally valid.
Let's recall some elements. Starting from HDL, synthesis is done in two main steps :
first, the VHDL is analyzed in order to detect RTL templates (consisting in RTL elements : flip-flops, arithmetic expressions, multiplexers , control logic ). We say that these elements are "infered" (i.e you must code using the right template to get what you wanted initially. You must imagine how these elements are connected, before coding ).
The second step is real logic synthesis, that takes a particular target technology parameters into account (types of gates available, timing, area, power).
These two steps clearly separates RTL functional needs (steering logic, computations) from technology contingencies (timing etc).
Let's come back to the first step (RTL) :
Concerning multiplexers, several coding styles are possible :
using concurrent assignement :
y<= a1 when cond1 else a2 when cond2 else cond3;
using if statement within a process :
process(a1,a2,a3,cond1,cond2)
begin
if(cond1) then
y<=a1;
elsif(cond2) then
y<=a2;
else
y<=a3;
end if;
end;
using another concurrent assignment
form, suitable for generic
descriptions : if sel is an integer
and muxin an array of signals, then :
muxout <= muxin(sel); --will infer a mux
Note that the 3 coding styles always work. Note also that they are "a bit more" than simple multiplexer as the coding style force the presence of a priority encoding (if elsif, when else), which is not the case of a simple equation-based multiplexer, really symmetric.
using a case statement
process(a1,a2,a3,cond1,cond2)
variable cond : std_logic(1 downto 0);
begin
cond := cond2 & cond1;
case cond is
when "01" => y<= a1;
when "10" => y<= a2;
when others => y<=a3;
end case;
end;
using a select statement (in our
example, two concurrent assignements
needed) :
sel <= cond2 & cond1;
WITH sel SELECT
y <= a1 WHEN "01",
a2 WHEN "10",
a3 WHEN OTHERS;
A final remark is about the rising of abstraction, even for RTL design : the synthesizers are now really mature. Have a look at Jiri Gaisler coding styles for LEON2 open source processor for example, as well as his coding styles (see here). He prones a very different approach, yet perfectly valid, from classical books.
You should always understand what the RTL synthesizer will infer.
In the contrary, behavioral synthesis allows you to forget (partially) what the synthesizer will infer. But that's another story.

Keeping time using timer interrupts an embedded microcontroller

This question is about programming small microcontrollers without an OS. In particular, I'm interested in PICs at the moment, but the question is general.
I've seen several times the following pattern for keeping time:
Timer interrupt code (say the timer fires every second):
...
if (sec_counter > 0)
sec_counter--;
...
Mainline code (non-interrupt):
sec_counter = 500; // 500 seconds
while (sec_counter)
{
// .. do stuff
}
The mainline code may repeat, set the counter to various values (not just seconds) and so on.
It seems to me there's a race condition here when the assignment to sec_counter in the mainline code isn't atomic. For example, in PIC18 the assignment is translated to 4 ASM statements (loading each byte at the time and selecting the right byte from the memory bank before that). If the interrupt code comes in the middle of this, the final value may be corrupted.
Curiously, if the value assigned is less than 256, the assignment is atomic, so there's no problem.
Am I right about this problem?
What patterns do you use to implement such behavior correctly? I see several options:
Disable interrupts before each assignment to sec_counter and enable after - this isn't pretty
Don't use an interrupt, but a separate timer which is started and then polled. This is clean, but uses up a whole timer (in the previous case the 1-sec firing timer can be used for other purposes as well).
Any other ideas?
The PIC architecture is as atomic as it gets. It ensures that all read-modify-write operations to a memory file are 'atomic'. Although it takes 4-clocks to perform the entire read-modify-write, all 4-clocks are consumed in a single instruction and the next instruction uses the next 4-clock cycle. It is the way that the pipeline works. In 8-clocks, two instructions are in the pipeline.
If the value is larger than 8-bit, it becomes an issue as the PIC is an 8-bit machine and larger operands are handled in multiple instructions. That will introduce atomic issues.
You definitely need to disable the interrupt before setting the counter. Ugly as it may be, it is necessary. It is a good practice to ALWAYS disable the interrupt before configuring hardware registers or software variables affecting the ISR method. If you are writing in C, you should consider all operations as non-atomic. If you find that you have to look at the generated assembly too many times, then it may be better to abandon C and program in assembly. In my experience, this is rarely the case.
Regarding the issue discussed, this is what I suggest:
ISR:
if (countDownFlag)
{
sec_counter--;
}
and setting the counter:
// make sure the countdown isn't running
sec_counter = 500;
countDownFlag = true;
...
// Countdown finished
countDownFlag = false;
You need an extra variable and is better to wrap everything in a function:
void startCountDown(int startValue)
{
sec_counter = 500;
countDownFlag = true;
}
This way you abstract the starting method (and hide ugliness if needed). For example you can easily change it to start a hardware timer without affecting the callers of the method.
Write the value then check that it is the value required would seem to be the simplest alternative.
do {
sec_counter = value;
} while (sec_counter != value);
BTW you should make the variable volatile if using C.
If you need to read the value then you can read it twice.
do {
value = sec_counter;
} while (value != sec_counter);
Because accesses to the sec_counter variable are not atomic, there's really no way to avoid disabling interrupts before accessing this variable in your mainline code and restoring interrupt state after the access if you want deterministic behavior. This would probably be a better choice than dedicating a HW timer for this task (unless you have a surplus of timers, in which case you might as well use one).
If you download Microchip's free TCP/IP Stack there are routines in there that use a timer overflow to keep track of elapsed time. Specifically "tick.c" and "tick.h". Just copy those files over to your project.
Inside those files you can see how they do it.
It's not so curious about the less than 256 moves being atomic - moving an 8 bit value is one opcode so that's as atomic as you get.
The best solution on such a microcontroller as the PIC is to disable interrupts before you change the timer value. You can even check the value of the interrupt flag when you change the variable in the main loop and handle it if you want. Make it a function that changes the value of the variable and you could even call it from the ISR as well.
Well, what does the comparison assembly code look like?
Taken to account that it counts downwards, and that it's just a zero compare, it should be safe if it first checks the MSB, then the LSB. There could be corruption, but it doesn't really matter if it comes in the middle between 0x100 and 0xff and the corrupted compare value is 0x1ff.
The way you are using your timer now, it won't count whole seconds anyway, because you might change it in the middle of a cycle.
So, if you don't care about it. The best way, in my opinion, would be to read the value, and then just compare the difference. It takes a couple of OPs more, but has no multi-threading problems.(Since the timer has priority)
If you are more strict about the time value, I would automatically disable the timer once it counts down to 0, and clear the internal counter of the timer and activate once you need it.
Move the code portion that would be on the main() to a proper function, and have it conditionally called by the ISR.
Also, to avoid any sort of delaying or missing ticks, choose this timer ISR to be a high-prio interrupt (the PIC18 has two levels).
One approach is to have an interrupt keep a byte variable, and have something else which gets called at least once every 256 times the counter is hit; do something like:
// ub==unsigned char; ui==unsigned int; ul==unsigned long
ub now_ctr; // This one is hit by the interrupt
ub prev_ctr;
ul big_ctr;
void poll_counter(void)
{
ub delta_ctr;
delta_ctr = (ub)(now_ctr-prev_ctr);
big_ctr += delta_ctr;
prev_ctr += delta_ctr;
}
A slight variation, if you don't mind forcing the interrupt's counter to stay in sync with the LSB of your big counter:
ul big_ctr;
void poll_counter(void)
{
big_ctr += (ub)(now_ctr - big_ctr);
}
No one addressed the issue of reading multibyte hardware registers (for example a timer.
The timer could roll over and increment its second byte while you're reading it.
Say it's 0x0001ffff and you read it. You might get 0x0010ffff, or 0x00010000.
The 16 bit peripheral register is volatile to your code.
For any volatile "variables", I use the double read technique.
do {
t = timer;
} while (t != timer);